I live in the USA so my house's electric service is 240V split single phase. The main breaker on the service panel is 200A.
But 200 amps at 240 volts is 48kVA. The pole pig feeding my house is 25kVA, and there are three other houses (4 houses total) connected to it. I assume this is fine because most houses will run high-power appliances at different times, and the transformer is probably rated to handle some excess load in cases of overlap.
I say our pole pig is 25kVA because there's a big "25" on the side of it. Generally, in most cases that number seems to be the kVA rating.
What happens if I decide to be stupid and build something big that's capable of pulling 200A and running my service flat out? Wouldn't that be likely to cook the transformer? I don't think my neighbors (or the electric company) would appreciate pole pig bacon for dinner, even though the explosion would probably be pretty cool.
It seems like these houses should be on a 50kVA transformer for better safety margin. The transformer that used to feed our house actually did explode, but I think it was pretty old. That was probably 20 years ago, so the "current" transformer has been working for that long.
But 200 amps at 240 volts is 48kVA. The pole pig feeding my house is 25kVA, and there are three other houses (4 houses total) connected to it. I assume this is fine because most houses will run high-power appliances at different times, and the transformer is probably rated to handle some excess load in cases of overlap.
I say our pole pig is 25kVA because there's a big "25" on the side of it. Generally, in most cases that number seems to be the kVA rating.
What happens if I decide to be stupid and build something big that's capable of pulling 200A and running my service flat out? Wouldn't that be likely to cook the transformer? I don't think my neighbors (or the electric company) would appreciate pole pig bacon for dinner, even though the explosion would probably be pretty cool.
It seems like these houses should be on a 50kVA transformer for better safety margin. The transformer that used to feed our house actually did explode, but I think it was pretty old. That was probably 20 years ago, so the "current" transformer has been working for that long.